09-18-2009, 09:12 PM
|
 |
Most Confused!
|
|
Join Date: Oct 2005
Location: Warren, MI
Posts: 2,769
|
|
Re: motor values
Quote:
|
Originally Posted by puckman
I was just wondering if anyone knows where I can get a list or info about the lowest / safest meg reading for 480 volt motors? I made a couple of calls where the motors were taken out of service because my 1587 came up .7 megs and the voltage would not reach 1000s. My boss asked me what the lowest reading should be and I told him 1 meg. not sure about that . 40 hp.
thanks for any help
|
The old handbook which is a bit outdated, some say, "A Stitch in Time" Megger/Biddle states the following.
Insulation resistance should be approximately one megohm for each 1,000
volts of operating voltage, with a minimum value of one megohm
__________________
Bill
|